The equipment grounding conductor must be bonded to the box and not rely on the device for the bonding connection. (See 250.148(B))

Chris
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
but what is a self grounding gfi outlet is use as per 250.146 D



Self grounding will have a tension piece where the mounting screw penatrates the yoke instead of an insulator. The insulator can be removed and perform the same function
 

raider1

Senior Member
Staff member
Location
Logan, Utah
but what is a self grounding gfi outlet is use as per 250.146 D

That section permits self grounding GFCI receptacles to be used without a bonding jumper between the receptacle and the metal box.

The metal box must always be bonded to the equipment grounding conductor directly and not through a device such as a receptacle.

Again I will reference 250.148 and specifically 250.148(B) for grounding continuity.