From my buddy at UL: GFCIs can be tested for 10kA SCCR if the manufacturer wants. No SCCR rating for standard receptacles.
From my buddy at UL: GFCIs can be tested for 10kA SCCR if the manufacturer wants. No SCCR rating for standard receptacles.
Why wouldn't it be important for any plug that is put in and out of a receptacle? A catestrophic failure would be bad news.there probably are some industrial control panels where it might matter, such as cases where a receptacle is provided for a motor to be plugged in. not that rare of a situation.
From my buddy at UL: GFCIs can be tested for 10kA SCCR if the manufacturer wants. No SCCR rating for standard receptacles.
Why wouldn't it be important for any plug that is put in and out of a receptacle? A catestrophic failure would be bad news.
A plug is often used as a disconnect or switch.I think a plug is roughly similar to a connector. connectors and conductors are not required to have SCCR ratings. I think only devices that can switch power can even have a rating at all.
I think a plug is roughly similar to a connector. connectors and conductors are not required to have SCCR ratings. I think only devices that can switch power can even have a rating at all.
A plug is often used as a disconnect or switch.