If a room telecom room is being put together what is ok for bonding the Rack? Can you go to the nearest panel?
I've never understood why a rack with no power connections would need to be grounded.
we typicaly run a bare #6 around the rack and any cable tray, bonding it to everything and then back to the panel serving that room.
Usually, it's not that the rack needs a connection to the GES for fault protection (the EGC takes care of that), but that it need to be bonded to it's fellow racks for signal integrity. That's a big concern in analog audio/video setups and others where signals use a ground reference.
Seems like a design decision and not a safety one (e.g. an ethernet patch rack with nothing but punchdown blocks or plastic feedthrus -- why should that rack be bonded)?
This paper from who else? a rack company! Has several pages on rack power and grounding.
http://www.middleatlantic.com/pdf/PowerPaper.pdf