I Installed 4x4 metal boxes with single gang flat mod rings on the surface a concrete wall, installation didn't pass the electrical rough inspection, because the flat mod rings, any advise on this? inspector didn't like the flat mod ring because it gonna be behind the drywall!, now I think on use extension boxes after the drywall installation to meet the code and install the receptacles.
I got this in mind. 1 ship the concrete wall and reinstall all the boxes with the required mod rings or 2 use extension boxes. please help.
View attachment 7375
Is the surface of the concrete wall also the finished wall?
Is the flat mud ring listed?
from the UL White Book:
METALLIC OUTLET BOXES (QCIT)
GENERAL
This category covers metallic mud rings, flush device boxes, conduit bodies,
conduit boxes, floor boxes, outlet boxes, outlet box hoods, special-purpose
boxes, extension rings, covers, and cover plates for flush-mounted
wiring devices, intended for installation in accordance with Article 314 of
ANSI/NFPA 70, ??National Electrical Code?? (NEC). These products are also
intended for installation and use in accordance with the following information.
MUD RINGS
A mud ring positions a flush-mounted wiring device flush with the finished
wall surface. Mud rings may be provided with either a fixed or
adjustable depth sleeve.
If you are positioning a flush mounted device with a mud ring that has zero extension because the finished surface is flush with the edge of the box, then I don't understand the problem the inspector claims.