malachi constant
Senior Member
- Location
- Minneapolis
I have a client that wants to add a "30A/2P 208V" stacked washer/dryer to each of 60 dwelling units. There are 360 units in the building, so 300 will not get the laundry. I'm assuming a load of 5000VA for the washer/dryer.
I assume they will also have to add the 20A/1P laundry receptacle.
I have collected all information about existing appliance nameplate data, unit panel/breaker information, and service size. I also have the "house load" utility info from last twelve months.
Each unit is roughly 1100 SF and includes an existing garbage disposal (672VA), dishwasher (1152 VA), range (8000VA), microwave (1800VA). That's about it.
FYI, two important things to note that I am not used to seeing:
1. There is not any AC or electric heat in a given unit - it is a centralized HVAC system with each unit containing a 1/20HP 1A booster/circulating fan.
2. The unit panels are each protected by 80A breakers.
There are two relevant calculations that need to be made: unit panel loads, and overall building service loads.
Unit loads is easy - follow 220.83 Existing Dwelling Unit, (A)-no additional HVAC installed. For a given unit add up your 3VA/SF general lighting, small appliance branch circuit, laundry branch circuit, and nameplate data. Without showing my math for an 1150 SF unit I'm getting 66A on an 80A panel. No problems here.
Service loads is where I think I am doing it right, but shocked at the number. As there is no heating/cooling and these are 80A panels I cannot use optional calcs, so I am going through standard calcs:
* 220.42 - 3VA/SF, demand factors per table 220.42, between about 1050SF/unit x 360 units works out to about 300kVA after demand factors.
* 220.52 - 3000VA per unit x 360 units for small appliance, 1500VA per unit x 60 units for laundry is 1,170kVA.
* 220.53 - 75% demand factor applied to dishwasher, disposal and circ fan - 360 of each - 525kVA.
* 220.54 - dryers - only 60 of them x 5000, demand factor of 25% = 75kVA. I believe I can apply another 70% demand factor per 220.61(B) = 53kVA
* 220.55 - 360 x 8000 x 0.16 for ranges = 461kVA, 360 x 1800 x 0.30 for microwaves = 195kVA, so 655kVA total for this. I believe I can apply another 70% demand factor per 220.61(B) = 459kVA.
When I add those up I get 2495kVA, or 6928 amps at 208V/3P. This does not count house loads, which are approximately another 800A (x 125% per 220.87(2)). I am told there is one service to the building for both house and dwelling loads combined, and it is rated for 4000A. Even when I delete the washer/dryer and laundry branch circuit I get 6500A (again, not including house). Am I doing something wrong here? Can someone do a quick walk through the numbers and see if there is something off? Is there a better way to calculate, more ways to derate, etc?
Thanks!!
(edited - found a calc error - was counting 1500VA laundry branch circuits in 360 units instead of just the 60 units)
I assume they will also have to add the 20A/1P laundry receptacle.
I have collected all information about existing appliance nameplate data, unit panel/breaker information, and service size. I also have the "house load" utility info from last twelve months.
Each unit is roughly 1100 SF and includes an existing garbage disposal (672VA), dishwasher (1152 VA), range (8000VA), microwave (1800VA). That's about it.
FYI, two important things to note that I am not used to seeing:
1. There is not any AC or electric heat in a given unit - it is a centralized HVAC system with each unit containing a 1/20HP 1A booster/circulating fan.
2. The unit panels are each protected by 80A breakers.
There are two relevant calculations that need to be made: unit panel loads, and overall building service loads.
Unit loads is easy - follow 220.83 Existing Dwelling Unit, (A)-no additional HVAC installed. For a given unit add up your 3VA/SF general lighting, small appliance branch circuit, laundry branch circuit, and nameplate data. Without showing my math for an 1150 SF unit I'm getting 66A on an 80A panel. No problems here.
Service loads is where I think I am doing it right, but shocked at the number. As there is no heating/cooling and these are 80A panels I cannot use optional calcs, so I am going through standard calcs:
* 220.42 - 3VA/SF, demand factors per table 220.42, between about 1050SF/unit x 360 units works out to about 300kVA after demand factors.
* 220.52 - 3000VA per unit x 360 units for small appliance, 1500VA per unit x 60 units for laundry is 1,170kVA.
* 220.53 - 75% demand factor applied to dishwasher, disposal and circ fan - 360 of each - 525kVA.
* 220.54 - dryers - only 60 of them x 5000, demand factor of 25% = 75kVA. I believe I can apply another 70% demand factor per 220.61(B) = 53kVA
* 220.55 - 360 x 8000 x 0.16 for ranges = 461kVA, 360 x 1800 x 0.30 for microwaves = 195kVA, so 655kVA total for this. I believe I can apply another 70% demand factor per 220.61(B) = 459kVA.
When I add those up I get 2495kVA, or 6928 amps at 208V/3P. This does not count house loads, which are approximately another 800A (x 125% per 220.87(2)). I am told there is one service to the building for both house and dwelling loads combined, and it is rated for 4000A. Even when I delete the washer/dryer and laundry branch circuit I get 6500A (again, not including house). Am I doing something wrong here? Can someone do a quick walk through the numbers and see if there is something off? Is there a better way to calculate, more ways to derate, etc?
Thanks!!
(edited - found a calc error - was counting 1500VA laundry branch circuits in 360 units instead of just the 60 units)