johnmccoll
Member
- Location
- Cody, WY, USA
I am working on an industrial MCC. 480V, 600A, parallel 500kcmil feeders to a 600 amp breaker. The load side of the breaker feeds a 600amp transfer switch and is fed with parallel 4/0 copper. My recommendation was to upsize these 4/0 conductors to parallel 350kcmil and have met with some resistance from the engineers. The 4/0 feeds are about 10' long, but a don't consider this a tap. They are also 120 degree rated, however the terminations on both ends are rated at 75 degrees. Am I missing something someplace which allows for this or is it how I believe and the engineers are suggesting I create a intentionally dangerous situation? I also should add that the feeder conductors show considerable heat damage and the breaker failed to trip on test which suggests to me the potential that this service has exceeded 600amps may exist. Thanks for the help!