Meeting the requirements of 517.13(A) and (B) has nothing to do with Mechanical Protection of the Emergency System, this must be done with one of the five methods prescribed in 517.30(C)(3) and where flexible wiring methods are allowed is covered in the 4 conditions of 517.30(C)(3)(3). The requirements of 517.13(A) will have to be done with a non-flexible wiring method in this case.if you read this article carefully, it points you to 517.13 a and b.. and B states that all luminaires above 7.5 feet are in the exception.. it then points you to 250.118 which says that a fixture whip is fine. also hospital work has been my bread and butter for the last 5 years or so and yes, inspectors have brought this up.Then I show them this and everything is fine..... now as for a under cabinet light, theres a differnt story??????![]()
Has anyone else had any experience with this issue?
Emergency fixture in Hospital. "Use of Flex whip not permitted for 2' x 4' Drop in fixture in T-Bar ceiling".
In my way of thinking The fixture is UL listed with a flexible whip attached.
I would think that would get me through 517.30(c)(3)(3)d.
The inspector does not agree and thinks I should remove the whip and hard pipe.
For me to modify the fixture and hard pipe seems blatantly wrong.
Not that it is right or wrong, but I have never hard pipe anything in a T-bar ceiling.
It seems to me there needs to be some seismic isolation in that situation.
I think you might be right and common sense is the issue.
The ones that I have seen hard piped used a 1900 box on the top of the fixture. The branch circuit conductors were spliced to the fixture wires in the 1900 box. The box was installed on the "wiring port" cover using a chase nipple.I assume you are entering the end so the wiring port can be opened.