Tamper Resistant Receps - above counter top

Status
Not open for further replies.

dana1028

Senior Member
Why are you even worrying about it. I don't even stock non TR anymore but technically you are probably correct.

Because I am in inspector - and believe the above installation [no TR receptacle in the cabinet above the counter] is compliant; thus no correction notice to change. Just wanting to make sure I'm not missing something.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
Because I am in inspector - and believe the above installation [no TR receptacle in the cabinet above the counter] is compliant; thus no correction notice to change. Just wanting to make sure I'm not missing something.

dana, 2011 406.12 Tamper Resistant Receptacles for Dwelling Units. A "non" Tamper resistant outlet in a closet or cabinet unless it is 5 and 1/2 feet above the floor would be non compliant.


406.12 Tamper-Resistant Receptacles in Dwelling Units. In all areas specified in 210.52, all nonlocking-type 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.
Exception: Receptacles in the following locations shall not be required to be tamper-resistant:

  1. Receptacles located more than 1.7 m (5? ft) above the floor. 70-273
  2. Receptacles that are part of a luminaire or appliance.
  3. A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7). or (A)(8).
  4. Nongrounding receptacles used for replacements as permitted in 406.4(D)(2)(a).
 

jumper

Senior Member
dana, 2011 406.12 Tamper Resistant Receptacles for Dwelling Units. A "non" Tamper resistant outlet in a closet or cabinet unless it is 5 and 1/2 feet above the floor would be non compliant.


406.12 Tamper-Resistant Receptacles in Dwelling Units. In all areas specified in 210.52, all nonlocking-type 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.
Exception: Receptacles in the following locations shall not be required to be tamper-resistant:

  1. Receptacles located more than 1.7 m (5? ft) above the floor. 70-273
  2. Receptacles that are part of a luminaire or appliance.
  3. A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7). or (A)(8).
  4. Nongrounding receptacles used for replacements as permitted in 406.4(D)(2)(a).

But 210.52 says that receptacles in a cabinet are not covered in this section.

210.52 Dwelling Unit Receptacle Outlets. This section
provides requirements for 125-volt, 15- and 20-ampere receptacle
outlets. The receptacles required by this section
shall be in addition to any receptacle that is:

(3) Located within cabinets or cupboards.............
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
But 210.52 says that receptacles in a cabinet are not covered in this section.

210.52 Dwelling Unit Receptacle Outlets. This section
provides requirements for 125-volt, 15- and 20-ampere receptacle
outlets. The receptacles required by this section
shall be in addition to any receptacle that is:

(3) Located within cabinets or cupboards.............


That is correct I could not edit, in the cabinet or above 5 and 1/2 not required but is not listed under 406.12
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
Sorry didn't read the whole thread, so if this was already answered I apologize. In the 2008 code there are no exceptions. If you are under the 2011 then you get the exceptions.
 