- Lockport, IL
- Semi-Retired Electrical Engineer
I was reminded this morning by the following quote that I wanted to post a question of my own.
http://forums.mikeholt.com/showthread.php?t=147660
I have a similar situation, one in which the owner wants a generator to supply the entire load of the building. It is not a dwelling unit, and the system will fall under 702 (optional standby). Can I bring both the utility service and the generator output directly to the ATS, and let the ATS serve as the building?s required disconnecting means?
From the comment I quoted above, I infer that I can specify an ATS that has the appropriate listing. I also infer that a "service-rated ATS" would have a method of bonding Neutral to Ground, a place to connect the GEC, and a method of providing separate N and G conductors downstream from that point. But how does it function as a disconnecting means? Does the ATS simply need a mid-position for OFF (and be lockable in that position)? Is there a separate breaker downstream of the transfer portion of the device, but within the same enclosure, so that that constitutes the building?s disconnecting means?
It came from this thread:. . . the transfer switch is service rated with a disconnecting means. GEC is relocated to the ATS.