Do you think about:
(B) Electrode Spacing. Where more than one of the electrodes
of the type specified in 250.52(A)(5) or (A)(7) are
used, each electrode of one grounding system (including
that used for strike termination devices) shall not be less
than 1.83 m (6 ft) from any other electrode of another
grounding system. Two or more grounding electrodes that
are bonded together shall be considered a single grounding
electrode system.
Also.
How do I do this with a city water supply using copper?
Not sure what you're getting at with the 6' reference. That reference is for two different grounding systems.