I have a situation where I'm sizing a panel/feed to connect (10) 1KW wind generators grid-tied to a large commercial facility. The output of each of the (10) inverters is 277V. My question has to do with Article 705.12:
How do I size the feeder and panel bus to feed the (10) inverters? Each wind generator would have a 277V, 20A circuit going to it from a 277/480V, 3-phase panel.
Do I have to comply with the 120% rule, in which case, I'd have to multiple 20amps*10*120%? = 250 panel and feeder? That seems ridiculous, given the generating capacity is less than 15 amps at 480v, 3-phase.
Please let me know where (or if) I'm going wrong here.