COMMENT 0-0 XXX.120 Correlation problem

Status
Not open for further replies.

fmtjfw

Senior Member
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 0-0 344.120. Thanks, Jim Williams

4 Comment:
revise text as below:

344.120 Marking. Each length shall be clearly and durably identified in every 3 m (10 ft) as required in the first sentence of 110.21(A). Nonferrous conduit of corrosion-resistant material shall have suitable markings.

5 Statement of Problem and Substantiation.

110.21 is now devoid of text, the text is now in 110.21(A).
 

fmtjfw

Senior Member
COMMENT 0-0 352.120 Correlation problem

COMMENT 0-0 352.120 Correlation problem

I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 0-0 352.120. Thanks, Jim Williams

4 Comment:
revise the text as follows:

352.120 Marking. Each length of PVC conduit shall be clearly and durably marked at least every 3 m (10 ft) as required in the first sentence of 110.21(A). The type of material shall also be included in the marking unless it is visually identifiable. For conduit recognized for use aboveground, these markings shall be permanent. For conduit limited to underground use only, these markings shall be sufficiently durable to remain legible until the material is installed. Conduit shall be permitted to be surface marked to indicate special characteristics of the material.

5 Statement of Problem and Substantiation.

110.21 is now devoid of text, the text is now in 110.21(A).
 

fmtjfw

Senior Member
COMMENT 0-0 355.120 Correlation problem

COMMENT 0-0 355.120 Correlation problem

I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 0-0 355.120. Thanks, Jim Williams

4 Comment:
revise the text as follows:

355.120 Marking. Each length of RTRC shall be clearly and durably marked at least every 3 m (10 ft) as required in the first sentence of 110.21(A). The type of material shall also be included in the marking unless it is visually identifiable. For conduit recognized for use aboveground, these markings shall be permanent. For conduit limited to underground use only, these markings shall be sufficiently durable to remain legible until the material is installed. Conduit shall be permitted to be surface marked to indicate special characteristics of the material.


5 Statement of Problem and Substantiation.

110.21 is now devoid of text, the text is now in 110.21(A).
 

fmtjfw

Senior Member
COMMENT 0-0 358.120 Correlation problem

COMMENT 0-0 358.120 Correlation problem

I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 0-0 358.120. Thanks, Jim Williams

4 Comment:
revise the text as follows:

358.120 Marking. EMT shall be clearly and durably marked at least every 3 m (10 ft) as required in the first sentence of 110.21(A).


5 Statement of Problem and Substantiation.

110.21 is now devoid of text, the text is now in 110.21(A).
 

fmtjfw

Senior Member
COMMENT 0-0 362.120 Correlation problem

COMMENT 0-0 362.120 Correlation problem

I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 0-0 362.120. Thanks, Jim Williams

4 Comment:
revise the text as follows:

362.120 Marking. ENT shall be clearly and durably marked at least every 3 m (10 ft) as required in the first sentence of 110.21(A). The type of material shall also be included in the marking. Marking for limited smoke shall be permitted on the tubing that has limited smoke-producing characteristics.


5 Statement of Problem and Substantiation.

110.21 is now devoid of text, the text is now in 110.21(A).
 

fmtjfw

Senior Member
COMMENT 0-0 384.120 Correlation problem

COMMENT 0-0 384.120 Correlation problem

I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 0-0 384.120. Thanks, Jim Williams

4 Comment:
revise the text as follows:

384.120 Marking. Each length of strut-type channel raceways shall be clearly and durably identified as required in the first sentence of 110.21(A).

5 Statement of Problem and Substantiation.

110.21 is now devoid of text, the text is now in 110.21(A).
 
Status
Not open for further replies.