Alwayslearningelec
 - NJ
 - Estimator
Slang term is a back strap or sometimes called a conduit spacer, it goes behind the raceway. More prevalent on RMC installations than EMT.
What is the purpose of them? Is it just to keep the conduit from the wall? If so why just RMC for the most part? Thanks
in technical terms it is called a thingamajiggy.
for emt it is a type 1 thingamajiggy. for rigid it is a type 2. it is important to use the correct type.
Are thingamajiggys listed? I thought only whatmacallits, doodads, and gizmos were.![]()
It provides a space equivalent to the of the distance from the back of the box to the edge of the KO. The conduit can run straight into the box without the need for bending a box set.
Looks to me like that backstrap was used by a hack to keep the strap from falling into the big hole they made for the anchor, not to space the EMT off the wall. I would have use a suitably sized fender washer. Also, maleable backstraps are made to work with maleable straps, not stamped straps like that one.
-Hal
Pure speculation about the large hole...no?
I got you youngsters on this one ,,,its called a clampback and was originally intended to be used to keep rigid aluminum conduit off concrete surfaces as the concrete had a lot of chlorine/chlorides,,,,,,,,,,chlorine and aluminum was thought not to mix and would cause a lot of corrosion and concrete failures.Its a long standing running gun battle between the cement folks and the aluminum conduit makers.
Often specified in wash down areas of food processing plants.
LOL Lots of guessing going on here guys,,,,,here's the real answer.
I got you youngsters on this one ,,,its called a clampback and was originally intended to be used to keep rigid aluminum conduit off concrete surfaces as the concrete had a lot of chlorine/chlorides,,,,,,,,,,chlorine and aluminum was thought not to mix and would cause a lot of corrosion and concrete failures.Its a long standing running gun battle between the cement folks and the aluminum conduit makers. Its one of those things that will always be around and will probably never be agreed on.
Thats the true start of it all.
The Old Man said that:thumbsup:
THanks...visually(installed) how to you tell the difference between rigid galvanized and rigid aluminum?