Transfer Switch/Laod Center
Installing a residential 12kW standby generator with a 100A ATS/16 circuit load center.
When moving the esential circuits to new panel do associated grounds and neutrals
also have to be transfered? Manufacturers drawing do not show them be moved.
I believe so.
300.3(B) Conductors of the Same Circuit. All conductors of
the same circuit and, where used, the grounded conductor
and all equipment grounding conductors and bonding conductors
shall be contained within the same raceway, auxiliary
gutter, cable tray, cablebus assembly, trench, cable, or
cord, unless otherwise permitted in accordance with
300.3(B)(1) through (B)(4).