I'm looking at a MV transformer application and trying to determine the best way to adequestely protect the trasformer with the breaker on the secondary side.
The transformer in question is a 1500kVA 12.47kVpri - 480Vsec with a 5.75%Z. The fuse on the primary of the transformer is a 150A rated fuse. The secondary of the transformer is connected to a 4000A rated switchear with a 4000A main breaker. I'm trying to determine what to set the long time pickup of the seconedary breaker to in order to adequately protect the transformer.
From table 450.3(A) I see that the secondary breaker can be set to 125% of xfmr FLA for "any location" and 250% of xfmr FLA for a "supervised location". I typically set the secondary protection to 125% of transformer FLA which in this case would be about 2258A however my concern is that this pickup on the secondary would not allow the use of the full capacity of the 4000A rated switchgear.
Since this transformer is locaed in a a facility with qualified electricians this probably falls under the "supervised location" category and thus would allow the secondary protection to be set up to 250% and therefore allow the breaker to be set a 4000A and allow the full capacity of the switchgear. When looking at the 4000A breaker setting on a TCC it falls below the transformer damage curve except in the breakers long time pickup region where it crosses the damge curve.
As I type this I realize that since the primary fuses are within 250% of the transfoemr FLA then no secondary protection is required for a supervised location.
I'm curious to hear how others deal with secondary protection in such applications.
The transformer in question is a 1500kVA 12.47kVpri - 480Vsec with a 5.75%Z. The fuse on the primary of the transformer is a 150A rated fuse. The secondary of the transformer is connected to a 4000A rated switchear with a 4000A main breaker. I'm trying to determine what to set the long time pickup of the seconedary breaker to in order to adequately protect the transformer.
From table 450.3(A) I see that the secondary breaker can be set to 125% of xfmr FLA for "any location" and 250% of xfmr FLA for a "supervised location". I typically set the secondary protection to 125% of transformer FLA which in this case would be about 2258A however my concern is that this pickup on the secondary would not allow the use of the full capacity of the 4000A rated switchgear.
Since this transformer is locaed in a a facility with qualified electricians this probably falls under the "supervised location" category and thus would allow the secondary protection to be set up to 250% and therefore allow the breaker to be set a 4000A and allow the full capacity of the switchgear. When looking at the 4000A breaker setting on a TCC it falls below the transformer damage curve except in the breakers long time pickup region where it crosses the damge curve.
As I type this I realize that since the primary fuses are within 250% of the transfoemr FLA then no secondary protection is required for a supervised location.
I'm curious to hear how others deal with secondary protection in such applications.