dave h
- Bergen, New York
Pole lighting on a soccer field.
We have 6 poles with a total of 27, 1500 MH floods running at 120 volts. The one conduit with 4 - 3 phase, 4 wire circuits circuit we are having a problem with controls 4 of the poles. The lighting is on 60 amp contactors, one for each pole. the four we are concerned with have 5,4,4,5 fixtures.
When its raining the person(s) turning the lights off are reporting a loud bang and a large flash of sparks coming from the breakers in the panelboard and the gutter below the panelboard. Outsde the building a cover blew off a gutter and bend the lid up 1.5 inches. The first time this happened was last fall, testing was done and faults were found in the feeds as well as there being no grounding in the building. Grounding was installed and all new feeders installed to the poles.
The system worked fine untill the first day of a soaking rain, the lights operated for 3 to 4 hours, then as they were being turned off the explosion repeated happened. We were back the next day and ran every test I could on wiring and gounding, no problems at all.
This never causes a breaker to open from short circuit. And I can't get it repeat the explosion when we are testing. Each fixture is also fused at the pole base with 20 amp cartrige fuses.
Any suggestions as to what he problem could be?
Please send any suggestion....Thanks dave h