augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Ref: NEC 230.43
In the wording, LFMC is shown as permissible between raceways or raceway and service equipment. There is no mention of using it between a meter enclosure and service equipment.
Is that Code permissible and, if so, is bonding required.
I see no problem with it and no need for bonding as both enclosures are bonded but with the wording as it is, I feel I may be overlooking something.r
 
Last edited by a moderator:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Interesting that it only states between raceway and service equip. I cannot imagine why it cannot be used between the meter and service equipment and yes I believe it needs to be bonded just as any metal raceway would be required to be.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
(Thanks for the correction--it's early :) )
IYO, would a "bonding jumper" be required as noted in the Article ?
 