malachi constant
Senior Member
- Location
- Minneapolis
Title kind of says it all.
On a project I am engineering we are replacing an existing electrical water heater of unknown nameplate value (but we do know it has a 30A/2P breaker) with a new 5kW model. 5000VA / 208V / sqrt(1) x 1.25 = 30.048 amps. Man, would I would love to reuse that breaker and wire... But do I have to go up to a 35A breaker?
(And of course I would have the contractor field verify the wire is in good shape.)
On a project I am engineering we are replacing an existing electrical water heater of unknown nameplate value (but we do know it has a 30A/2P breaker) with a new 5kW model. 5000VA / 208V / sqrt(1) x 1.25 = 30.048 amps. Man, would I would love to reuse that breaker and wire... But do I have to go up to a 35A breaker?
(And of course I would have the contractor field verify the wire is in good shape.)