SparkyRules
 - United States
We are hooking up the utility interactive part of a PV system comprised of self contained AC inverter modules (output 240/120 AC volts each). The inverter is built into each module, so no separate inverter. So where is the ground fault detection? Is there a component missing? There is a combiner box which takes our 2- 240/120 inverter output circuits thru their own OC (breaker) then combines them into one inverter output circuit which is then backfeed thru  the house panel per 705-(D) (5) and (7). but said box is just 2- 2pole breakers in a 3R box. Could we use a "hot tub" GFI breaker ( like an HOM220GFI) for this if we spliced it between the PV modules and the house panel, with the line looking at the house panel and the load looking at the modules?  Would this not meet the intent of GF detection? How many MA are we trying to detect? per 690.6(D)? would this even work having current flowing backwards thru a GFI breaker? How many UL folks would it take to figure out if this was "listed" for this use? :happysad: Would this not also serve as the inverter disconnecting means (705.21)?