Because ampacity is in no way related to the voltage drop of a conductor due to any load current through it.  Period.  No ifs, ands, buts, or "excepts."
Here's another example.  #1THHN with 75 deg terminations has an ampacity of 130.  Compare the voltage drop on two feeders using #1 THHN:
The first feeder has a load current of 130Amps.  The second feeder has a load current of 120Amps.  Both feeders have the same ampacity, yet they will have a different voltage drop because they have different load currents.
Now compare a feeder with a 120A load current (130A ampacity) with a feeder with a 120A load current that shares a conduit with another feeder (6 current carrying conductors.)  The ampacity of the feeder in the shared conduit is 150*0.8=120.  The feeders have a different ampacity, yet they will have the some voltage drop because they have the same load currents.
So different load current with same ampacity = different voltage drop.  And different ampacity with the same load current = same voltage drop.  So do you see a relationship between load current and voltage drop, or between ampacity and voltage drop?