358.22 Number of Conductors.
The number of conductors shall not exceed that permitted by the percentage fill specified in Table 1, Chapter 9.
Cables shall be permitted to be installed where such use is not prohibited by the respective cable articles. The number of cables shall not exceed the allowable percentage fill specified in Table 1, Chapter 9.
I see it a lot too. Often times, judging by the work that I see, the work has done by electricians that apparently only carry romex in their truck.The question is why do you want to do so other than for limited portions where you are maybe providing physical protection?...
Most of time when I see it, it was done by some DYI or handiman that doesn't know any better....