I?m working up specifications for the installation and testing of cables for a ?Bid Specifications? document we provide to potential contractors. Below is an excerpt from the ?Termination and Testing? section.
? All circuits of voltage greater than or equal to 480VAC and having a current carrying capacity equal to or greater than 100 Amps or wire size equal to or greater than #4 AWG; shall be resistance tested between the current carrying conductors with a Meggar to 1000V prior to termination and energizing. The conductors must have a phase to phase resistance of greater than or equal to 5meg and a resistance greater than or equal to 20meg W to ground. Results of resistance tests shall be documented and provided to Customer.
Note, I?ve specified 5meg and 20meg for conductor to conductor and conductors to ground respectively. Would those numbers be considered acceptable for testing new cable installs?
I may also add procedures to test cables between Controllers (VFDs, Softstarts, etc) and Motors at less than 100 Amps and #4 AWG. But in these cases a Megger wouldn?t be required, only an Ohm Meter to confirm no Phase to Phase or to Ground shorts.
Looking for opinions or recommendations on such procedures or specifications.
Thanks
? All circuits of voltage greater than or equal to 480VAC and having a current carrying capacity equal to or greater than 100 Amps or wire size equal to or greater than #4 AWG; shall be resistance tested between the current carrying conductors with a Meggar to 1000V prior to termination and energizing. The conductors must have a phase to phase resistance of greater than or equal to 5meg and a resistance greater than or equal to 20meg W to ground. Results of resistance tests shall be documented and provided to Customer.
Note, I?ve specified 5meg and 20meg for conductor to conductor and conductors to ground respectively. Would those numbers be considered acceptable for testing new cable installs?
I may also add procedures to test cables between Controllers (VFDs, Softstarts, etc) and Motors at less than 100 Amps and #4 AWG. But in these cases a Megger wouldn?t be required, only an Ohm Meter to confirm no Phase to Phase or to Ground shorts.
Looking for opinions or recommendations on such procedures or specifications.
Thanks