A conduit body will only require support if it's larger than the trade size of the conduit when used with any of these raceways.
The exception you highlighted allows for support by only ONE raceway instead of the usual two or more if one of the raceways listed is used and if the conduit body does not contain devices, luminaires or lampholders. It says nothing that changes the distance to the first support, so the rules in the main article still apply
I don't see it, where in the exception does it say that?
I don't know what I was reading before - right now it looks like you are correct. Is early though so the brain is only half powered right now.
Great thread, but what have we learned? Can a "C" be used to "restart" a run when you're closing in on 360 degrees? Can they be an alternative to a (Straight) pull box/gutter? Do the answers to this depend on conductor size? Funny there's such confusion over this, such brain power and experience here at MH and still so many questions. This article needs some rewording as previously stated.
What would be your answers to the questions that you've come up with?![]()
Great thread, but what have we learned? Can a "C" be used to "restart" a run when you're closing in on 360 degrees? Can they be an alternative to a (Straight) pull box/gutter? Do the answers to this depend on conductor size? Funny there's such confusion over this, such brain power and experience here at MH and still so many questions. This article needs some rewording as previously stated.
Haha, I do believe a "C" can be used to help with the 360 degree rule as well as replace a pull box in certain conditions, I never questioned that until now. I enjoy learning so I'm curious if my thinking has been flawed.
Okay guys, let me sum this up. If the conductors being used are smaller than #4, a "C" can be used as a pulling point. If the conductors are #4 or larger, the "C" is almost worthless considering I don't recall ever seeing a "C" 8 x's the entry size in length. Are they made? Seems like the more expensive pull boxes or gutters would have to be used if one wanted to be code compliant. Sound correct?
Thanks Rob, I'm glad you bring that up because it means my usage of C's has been correct. For example, I just ran 1 1/4 pvc and the 1 1/4 C stated 3 #2's max, however I had three 12's and a #6 running through it so I stepped it up to an 1 1/2 C.
...but there is no provision in the code for the "unmarked" combintations.....There is not enough room to mark them with all the possible combinations that may be acceptable.
...but there is no provision in the code for the "unmarked" combinations.
That is correct, so am I in violation if I pull 20 - 10AWG in a conduit body marked 3-2AWG max? The "marked" combinations is pretty limiting compared to what the possibilities are for conductors in the raceways....but there is no provision in the code for the "unmarked" combintations.
That is correct, so am I in violation if I pull 20 - 10AWG in a conduit body marked 3-2AWG max? The "marked" combinations is pretty limiting compared to what the possibilities are for conductors in the raceways.
I am assuming you meant three #2 and not three 12's
That is where the problem with the markings on the conduit bodies comes in.
Did the 1-1/2 body you used mention more than 3 conductors?
There is not enough room to mark them with all the possible combinations that may be acceptable.
Since you chose #10 AWG conductors in your example you are not required to comply with the marking. The marking only applies to conductors #4 and larger.