Are normal power supply conductors permitted to share the same raceway, J-boxes, or wireways with generator load conductors? I've always thought it was against code until I saw normal supply conductors sharing a wireway with conductors from a back-up generator then became unsure of myself. Thanks.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Hello,

Are normal power supply conductors permitted to share the same raceway, J-boxes, or wireways with generator load conductors? I've always thought it was against code until I saw normal supply conductors sharing a wireway with conductors from a back-up generator then became unsure of myself. Thanks.

It depends how the generator supply system is classed. If this is an "Optional Standby System" (702) it is OK. See Art. 700,701 and 702.
 

kwired

Electron manager
Location
NE Nebraska
And in no case are they permitted together if the normal supply conductors are the service conductors - except at the service disconnect enclosure.
 