Generator Transfer Switch

Status
Not open for further replies.

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Yes, if it is SUSE rated as you indicate. You need to move the GES to the ATS and run a EGC to the old disconnect and remove the main bonding jumper though. Have you considered just removing the old service disconnect?
 