,,,,,,,,,,as a matter of routine way of doing things.
That was to use the ground conductors within a multiconductor tray cable as a return fault path from the equipment being served to the ground bus in the MCC.This was then extended to the transformer via cable bus or bus duct.When RMC was used a ground conductor was always pulled with the user conductors,,,,the conduit was not used for fault protection.
You know when you do something for 44 years it just becomes automatic whether it was spec'ed,an NEC requirement/recommendation or IEEE recommendation etc.
In reading over the many posts both residential and commercial on this and other forums it appears that the conduit was most often used for this purpose.I realize most of you folks are sometimes a one man operation and /or a small crew and material dollars would bend the allowed contract dollar.I normally didn't have to address that as the contract was bid and won to do as described above.
Now with all that being said I can't find a requirement thus far in looking in the NEC that requires this.It must be there somewhere or the cable manufacturers would not be putting those ground wires in the majority of standard cables.
I certainly feel as you do I'm sure, that a continuous cable from fault to voltage source is a more positive application of providing fault protection.
Where's the requirement written in NEC ?
dick
That was to use the ground conductors within a multiconductor tray cable as a return fault path from the equipment being served to the ground bus in the MCC.This was then extended to the transformer via cable bus or bus duct.When RMC was used a ground conductor was always pulled with the user conductors,,,,the conduit was not used for fault protection.
You know when you do something for 44 years it just becomes automatic whether it was spec'ed,an NEC requirement/recommendation or IEEE recommendation etc.
In reading over the many posts both residential and commercial on this and other forums it appears that the conduit was most often used for this purpose.I realize most of you folks are sometimes a one man operation and /or a small crew and material dollars would bend the allowed contract dollar.I normally didn't have to address that as the contract was bid and won to do as described above.
Now with all that being said I can't find a requirement thus far in looking in the NEC that requires this.It must be there somewhere or the cable manufacturers would not be putting those ground wires in the majority of standard cables.
I certainly feel as you do I'm sure, that a continuous cable from fault to voltage source is a more positive application of providing fault protection.
Where's the requirement written in NEC ?
dick