When calculating neutral load current, I was wondering how to calculate following samples:
In a 3-wire, 240/120V, single phase circuit with some unbalanceed loads, what is the neutral current? This sample is only part of the panel board.
Phase A Phase B
Lighting Load 500W
Receptacle Load 360W
Clothes Dryer 2200W 2200W
I did like that : In = 500/120 + 360/120 = 7.2A
In a 4-wire, 208/120V, three phase circuit with some unbalanceed loads, what is the neutral current? This sample is only part of the panel board.
Phase A Phase B Phase C
Condening Unit 550W 650W
LOBBY 1500W
E-Elev 1100W 1100W
DHW PUMP 600W 600W 600W
I did like that : In = 550/120 + 650/120 + 1500/120 = 22.5A
Many thanks in advance