there is that spiffy derating that now takes place with
conduit on a roof, depending on how close to the roof
the conduit is....
THWN #6 copper stranded is rated for 65 amps,
according to my spiffy iphone app.....
in conduit 6" above the roof, that becomes 48.8 amps.
it's not till you get to 37" above the roof you get the
full rating back.
who's derating, and who's not? i'm just curious....