Double tapped GFCI Breaker
mjenn
New member
HI,
I am inspecting a home and noticed that the GFCI breaker appears to be double tapped on the black (hot) and triple tapped on the white (neutral). This is a 20 amp breaker connected to 14 AWG. Home inspectors don't uncover code violations but are required to document the finding for reference to a licensed electrician. For my own knowledge, I want to know if this is proper for Florida code.
Thanks for your support, great site!
Yes I agree that it has been "double tapped" and requires correction which could be a simple as two splices and pigtails and a 15 amp CB. The third white conductor is the neutral for the GFCI circuit breaker and is not under the same terminal. There are some CB's that are listed for two conductors but this isn't one of them. Also the #14 on a 20 amp OCPD is a problem.
Welcome to the Forum. :)
Usually it is just about impossible to get more than one conductor on the terminals of a GFCI breaker, so it is somewhat impressive that someone actually did it.