Yes, it is an exam question and Yes I can't find anything pertaining to that issue. That is the problem. And the answers were True or False....
Thanks, Stevareno
True' take a look at (D) 2
320.30 Securing and Supporting.
(A) General. Type AC cable shall be supported and secured by  staples, cable ties, straps, hangers, or similar fittings, designed and  installed so as not to damage the cable.
(B) Securing. Unless otherwise permitted,  Type AC cable shall be secured within 300 mm (12 in.) of every outlet  box, junction box, cabinet, or fitting and at intervals not exceeding  1.4 m (4? ft) where installed on or across framing members.
(C) Supporting. Unless otherwise permitted, Type AC cable shall be supported at intervals not exceeding 1.4 m (4? ft).
 Horizontal runs of Type AC cable installed in wooden or metal framing  members or similar supporting means shall be considered supported where  such support does not exceed 1.4-m (4?-ft) intervals.
(D) Unsupported Cables. Type AC cable shall be permitted to be unsupported where the cable complies with any of the following:
- Is fished between access points through concealed spaces in finished buildings or structures and supporting is impracticable
- Is not more than 600 mm (2 ft) in length at terminals where flexibility is necessary
- Is not more than 1.8 m (6 ft) in length from the last point of cable  support to the point of connection to a luminaire(s) or other  electrical equipment and the cable and point of connection are within an  accessible ceiling. For the purposes of this section, Type AC cable  fittings shall be permitted as a means of cable support.