Doc_Larry
 - New York City
I have a project where the homeowner wants to install a clothes dryer in an apartment that has a 60A service. The specific dryer manufacturer specifies the 120/240V 3-pole dryer load at 2,700VA and has provided an engineering technical memorandum that states that the dryer circuit may be protected by dual 15A breakers.
The 2011 code specifies that the dryer either be included as a 5,000 VA load in the Standard 220.42/220.52/220.54 calculation or (for this dryer) a 2,700VA load in the Optional 220.82 calculation. However, either way the calculated load exceeds the 60A service.
A third possible alternative is to consider the dryer service to be two additional 15A laundry circuits wired to provide a 3-pole, 4-wire 120/240V 15A supply. Doing it this way the dryer load is then included as 3,000VA, but it and all other loads above 3,000 VA will be subject to the 35% demand factor provided for in the standard calculation.
If the dryer circuit is accounted for as two additional laundry circuits, the calculated load is within the capability of the 60A service, but is this approach code compliant?