Ronnie...
Are you sure it is a 1 Hp shaded-pole motor?
Regards, Phil
It would be nice to have a picture of the NP on the motor itself.
Ronnie...
Are you sure it is a 1 Hp shaded-pole motor?
Regards, Phil
Ronnie...
Are you sure it is a 1 Hp shaded-pole motor?
Regards, Phil
It would be nice to have a picture of the NP on the motor itself.
A shaded-pole motor is basically a small squirrel-cage motor in which the auxiliary winding is composed of a copper ring or bar surrounding a portion of each pole.This auxiliary single-turn winding is called a shading coil. Currents induced in this coil by the magnetic field create a second electrical phase by delaying the phase of magnetic flux change for that pole (a shaded pole) enough to provide a 2-phase rotating magnetic field. The direction of rotation is from the unshaded side to the shaded (ring) side of the pole.
View attachment 7595
View attachment 7596
I think it's a valid point, but I also think it's possible that it is not 1HP, but 1/10th HP and says ".1HP" on the plate. I've seen that sort of thing happen a lot of small motors, I have had people INSIST that they had a 25HP 120V motor, when in fact is was .25HP...My contention is that a 1 Hp shaded-pole induction motor is unlikely to be chosen to drive a hood-vent blower!
Regards, Phil
I think it's a valid point, but I also think it's possible that it is not 1HP, but 1/10th HP and says ".1HP" on the plate. I've seen that sort of thing happen a lot of small motors, I have had people INSIST that they had a 25HP 120V motor, when in fact is was .25HP...
If it is 1HP, it probably is more likely a PSC motor. In OEM blower motors, the cap is often buried in the back of the motor so it looks exactly like a Shaded Pole from the outside.
Not to mention the exercise we get jumping to conclusions. :thumbsup:... But then all the fun would have been missed speculating.
If OP tells us shaft size (even if estimated) there will likely be an obvious difference between .1 Hp and 1.0 Hp.
A general idea of the size of the fan/blower wheel may make it fairly obvious also.
I kind of have a feeling if this fan were .10 Hp the OP would not have the noise problem that started this thread, and the speed control he is questioning is definitely more than needed if it is only .10 Hp.
No, you didn't miss it. The OP is AWOL.Did the OP post a picture of the NP on the motor which would resolve the speculation or did I miss it?
Did the OP post a picture of the NP on the motor which would resolve the speculation or did I miss it?
If you look at his posts again, he mentions it is for a couple who is now only cooking for two. That implies it is a residential cook top vent hood, 20" would be serious overkill, as would anything with a 1HP motor.No, but if we find out the motor only has a 3/16 inch shaft the likelihood of it being 1 hp is not very high.
Also if it has a 20 inch blower wheel, then the chance of it being successfully driven by a 1/10 hp motor is very unlikely, unless is turns really slow - then he would not have the noise issue though.
If you look at his posts again, he mentions it is for a couple who is now only cooking for two. That implies it is a residential cook top vent hood, 20" would be serious overkill, as would anything with a 1HP motor.
Then again, I have seen serious overkill in kitchen designs a lot lately. Just saw one with a walk-in freezer (and no, he is not a hunter or farmer, it was stocked with frozen pizzas and Costco meat from what I could see).
No, but if we find out the motor only has a 3/16 inch shaft the likelihood of it being 1 hp is not very high.
Also if it has a 20 inch blower wheel, then the chance of it being successfully driven by a 1/10 hp motor is very unlikely, unless is turns really slow - then he would not have the noise issue though.
It's almost as if he/she threw a grenade in our fox hole and ducked.
Anything requiring more than 1/4 HP motor is serious overkill for most dwelling unit cooking exhaust fan.
If indeed it is a 1 HP blower it is possibly trying to pull more air out than can come in - just allowing for make up air may help silence it some.
Sounds a little like one of those situations where "more power is better" and now they want to slow it down to cut down on noise - effectively making purchasing such a large unit a big waste of $$$.
"Honey, when the vent hood fan is running, I can't open the kitchen door!"