Mivey, I believe your are the one mistaken. My comments had nothing to do with any of your posts
.
Since you quoted Iwire's response to my post, it is only natural to think that it had something to do with my post. If you are talking about something completely different, then so be it and carry on.
This is hard to see but it states that the demand charge will be the highest average KW
measured during the 15 minute interal during the billing period and not chunks of energy..
You are misunderstanding what they are saying. They are saying the kW is an average obtained by taking the energy divided by the time. This gives you the average kW for the 15 minute interval. In other words, the thousands of readings are accumulating chunks of energy in registers. Each chunk represents the area under the kW vs time graph and is a chunk of energy.
To state it a different way: there is only one average kW for any 15 minute interval and that is the 15-minute energy divided by time. There are not multiple averages within the 15 minutes that you can search through to find a highest average. The "highest" comparison is made by comparing different 15 minute periods.
You could also say each chunk is the average demand over the fraction of a second that it represents. So you can see it does not make sense to refer to the highest average demand as being the highest of a bunch of averages within an individual interval.The "highest" they refer to is not the highest average inside the interval as that makes no sense and it not the way a meter works. By "highest" they mean the meter has a register that stores the highest 15 minute demand which is the average demand for the interval which is the energy in the interval divided by the time in the interval.
When the demand register is reset, the highest demand is zero. The first 15 minutes of energy is divided by the time and the register stores this as the highest demand (the average for the 15 minute period) because it is higher than zero. At the end of the second 15 minutes, the average demand is again calculated and compared to the register value. If the new average is higher, it replaces the old value in the register. This continues every 15 minutes until the demand register is reset.
National Grid's "the demand charge will be the highest average kW" means they do not use an instantaneous demand. They don't use one of the thousand of readings made per second. Supposed they used a 5-second average within the 15 minute interval. Then if they said they used the highest average within a 15-minute interval, that would simply mean they are using a 5-second demand interval across the whole billing period and the 15-minutes means nothing. Just think about the math. FWIW, even a 5 second demand is the Joules of energy consumed in 5 seconds divided by 5 seconds to give you J/s or watts.
Iwire's answer was wrong but his basic concept was not.
His basic concept considered the start time but not the motor run time he specified.