Rewire
Senior Member
- Location
- Lake of the Ozarks
has anyone installed one yet? How has it worked out?What is the cost?
I haven't seen them. I don't think they are on the market yet.
I dont think there is any benefit of having a AFCI receptacle, it just doesn't make sense.
they are cheaper than a breaker
They may be cheaper than the breaker but you have to comply with this.
210.12(B)
Exception No. 1: Where RMC, IMC, EMT or steel armored cable, Type AC, meeting the requirements of 250.118 using metal outlet and junction boxes is installed for the portion of the branch circuit between the branch-circuit overcurrent device and the first outlet, it shall be permitted to install a combination AFCI at the first outlet to provide protection for the remaining portion of the branch circuit.
has anyone installed one yet? How has it worked out?What is the cost?
they are cheaper than a breaker
One big advantage regardless of cost would be installation where you have a breaker panel where there is no AFCI's available to fit the panel, like Pushmatic, FPE, Zinsco...
dont get excited I was just assuming the cost would be kless as gfi recptacles are cheaper than breakers I should have placed a ? at the endYou asked what cost was in first post then later said they are cheaper than a breaker:?
..
dont get excited I was just assuming the cost would be kless as gfi recptacles are cheaper than breakers I should have placed a ? at the end
..........
This same concept is a good way to get around having to turn off all the conductors of MWBC's just to work on one.
Roger
Although I think AFCI's are most snake oil this will not be big deal in cases where a panel is located in a utility room or garage. I would simply mount an AFCI receptacle in a surface mounted box at the panel with a metallic nipple and connect the existing circuit conductors to the load side. Heck they should start making faceless versions for this type of installation where numerous circuits would need to be protected and multi-gang boxes could be located under or beside a panel.
This same concept is a good way to get around having to turn off all the conductors of MWBC's just to work on one.
Roger
You're missing the point, the handle ties would still be in place for 210.4 and you are correct that the dangers that were present before the 2008 requirement are back in play but, IMO even with that being the case, being able to isolate one conductor from the MWBC is probably better than working on it live which I think is done probably more now than pre handle tie requirement.I don't see it making any difference in the MWBC case. There is still risk of opening a neutral conductor that is carrying current and two pole breakers or handle ties would still be required.
Now I am missing your point. My point is the first device from the circuits origin is where the AFCI receptacle will have to be installed to meet 210.12(B) and the closer to the panel the better as far as protecting the whole circuit is concerned.Will these AFCI devices have a way to lock off power if used as a disconnecting means? Can they even be considered a disconnecting means?
You're missing the point, the handle ties would still be in place for 210.4 and you are correct that the dangers that were present before the 2008 requirement are back in play but, IMO even with that being the case, being able to isolate one conductor from the MWBC is probably better than working on it live which I think is done probably more now than pre handle tie requirement.
Now I am missing your point. My point is the first device from the circuits origin is where the AFCI receptacle will have to be installed to meet 210.12(B) and the closer to the panel the better as far as protecting the whole circuit is concerned.
I don't see where an AFCI receptacle would need to be handled any differently or considered a disconnecting means any differently than a standard receptacle would.
Roger
What I am trying to bring into the picture is the main reason for requiring simultaneous disconnection of all ungrounded conductors of a MWBC, as well as the fact that safe work practices dictates LOTO procedures. If this AFCI receptacle is similar in design to a GFCI (basically just a test and reset button for operator controls) How do you turn off a circuit and then ensure it can not be turned on by someone else while you are working on it? The circuit breaker versions do have attachment devices that can be used to lock them in the open position.
But I do agree any method of removing power is safer than not removing it at all. But OSHA does not really care that much even if a small effort was made, and if someone incidentally turns something on the electrons in the conductors do not care one bit, if there is continuity they are going to follow it.