CTs for two different instruments.

Status
Not open for further replies.
To build on Phil's statement:
Protection relays can be used with metering current transformers. Metering devices may not work well with protection CTs.

For precise results it is best to have separate CTs for each device.
Electronic and electromechanical devices may not play well together.
 
Another essential difference...

For 'protection', Metering CTs should saturation close to the nominal current it's required to measure! Ironic, isn't it!