Do You Like Ham
- TX, USA
I have a basic voltage drop question.
Part way through the following url:
http://ecmweb.com/code-basics/dont-let-voltage-drop-get-your-system-down
Is this example:
Let's do a sample calculation using the Ohm's Law method. What is the voltage drop of two 12 AWG THHN conductors that supply a 16A, 120V load located 100 feet from the power supply?
VD = I * R
I = 16A
R = 2 ohms/1000 ft (Chapter 9 Table 9)
CD = 16A * 2ohms/1000 ft * 200 ft = 6.4 V
Here, they doubled the length of the circuit when using the length.
Now, refer to:
http://www.eaton.com/ecm/groups/public/@pub/@electrical/documents/content/tb08104003e.pdf
Page 1.3-23, in the first column/big paragraph of text states:
"The circuit length is from the beginning point to the end point of the circuit regardless of the number of conductors"
Under the next column, Calculations section, #1, it states: "Circuit length is the distance from the point of origin to the load end of the circuit".
Compute the voltage drop for the same example above, using the details in the Eaton document:
Step 1:
Amps = 16A
Circuit length = 100 feet
Amps * Length = 1600 Amp Feet
Step 2:
Divide by 100
1600 / 100 = 16
Step 3:
0.3410 Voltage Drop - volts per Ampere per 100 feet (Table 1.3-13, on the next page).
(assume 1.0 PF, Steel conduit)
Multiply by VD value from table
0.3410 * 16 = 5.456
Multiply by 'Correction Factor'
Correction Factor = 0.577 (under the first column of text on the same page, under #2).
5.456 * 0.577 = 3.15 V
So, the question is, why does the Eaton approach result in a voltage drop about half that of the conventional wisdom that :
for single-pole line-to-neutral, one needs to use the 'back-and-forth' (2x) the circuit length? Is there something I'm overlooking in the Eaton documentation?
Is this example:
VD = I * R
I = 16A
Now, refer to:
Step 1:
Amps = 16A
Step 2:
Divide by 100
1600 / 100 = 16
Step 3:
0.3410 * 16 = 5.456