Customer called that he'd bought an exercise machine. Tech plugged it into the wall and burned up the display panel. I went out & got a no ground with my Wood head. Measured 120 hot to neutral, 80 some from neutral to ground and 30 some from hot to ground. After checking several receps on the ckt, I checked panel & found a broken ground wire. Missed it several times. The cable came in with several others, all grounds twisted together & wire nutted to a single #10 going to bar. I kept poking around & found this gnd looked part of the bundle, but was broken shortly into the mass of other wires. I terminated it securely & no further problem.
I had been expecting to find a broken neutral somewhere also. Most odd readings I've ever seen were from broken neutral or reversed neutral/ground. No load on ckt when I got those readings.
Anyone seen this before?
I had been expecting to find a broken neutral somewhere also. Most odd readings I've ever seen were from broken neutral or reversed neutral/ground. No load on ckt when I got those readings.
Anyone seen this before?