TimK
Member
- Location
- Tacoma, WA
Would a parallel run within the same conduit be the only time the grounding conductor is the largest conductor? Excluding specs and special engineering of course.
Maybe I am misunderstanding your question but I can't see even in a single conduit parallel instalation where the EGC would be larger than the ungrounded conductors.Would a parallel run within the same conduit be the only time the grounding conductor is the largest conductor? Excluding specs and special engineering of course.
Mark, can you give an example of where that might be the case?If you're trying to use one grounding conductor instead of 2 parallel ones, then it could be the largest one.
As Travish points out, you can not parallel conductors (excluding some exceptions) smaller than 1/0Well, not that it is done often with smaller wires, but instead of 3/0 copper, we run parallel #3's to the service, now if I install them in the same conduit wouldn't my grounding conductor need to be #2?
I guess I am thinking more of grounding and not equipment grounding.
Well, let me do some reading then, maybe I am thinking of grounded, or am i chasing my tail on that one also?:ashamed:
Maybe it is parallel runs in parallel conduits that you are thinking of? For example, 7 parallel 1/0 runs in 7 conduits, protected by a 1000 amp breaker would require a 2/0 equipment ground in each conduit.
I used to think that an egc could be larger than the conductors in a parallel run and I even wrote a proposal about it. The comment was the egc never has to be larger than the CCC.
My understanding is that the egc in each conduit would never need to be bigger than the CCC. So 1/0 egc is all that is needed if the CCC was 1/0- the 2/0 is not necessarySo does that mean I am wrong in my last statement?
My understanding is that the egc in each conduit would never need to be bigger than the CCC. So 1/0 egc is all that is needed if the CCC was 1/0- the 2/0 is not necessary
Yes but look at 250.122(A)IAW 250.122(F) it needs to be sized off the OCPD does it not?
Yes but look at 250.122(A)
I could agree, and I know it does not say "accumulative" but I always took that as the total cross sectional.
The conductors in each conduit is being protected for ground fault. If the EGC is the same size as the CCC then it will have the protection for those conductors. That is how I see it.