Dennis, just as with Doctors, don't put them on a pedestal or assume they are always right simply because of a title.Many of these guys are engineers so I am assuming they know what they are talking about. Oh well....
Roger
Roger
That's the truth. Not sure I had him on a pedestal but perhaps there was something to it. I just didn't quite understand what was being explained so I gave him the benefit of the doubt. Heck I am just a lonely EC...![]()
If you are standing on the earth a couple of feet away from the energized fence and not on top of a bonding conductor in the earth, you will get a shock of ~50% of the voltage that is on the fence. The earth is not a good enough conductor to create the "bird on a wire" effect. For that effect to work you have to be able to raise the voltage of the earth to match that of the fence. Grounding and bonding does nothing to remove the voltage on the fence, other than to provide a low impedance fault path so that the OCPD will trip.... The fence was mentioned and the guy said if you were touching the fence with your hands and your feet was on the ground, you would be shocked. In my thinking, the fence, if metal, would be bonded too and you would have the "bird on the wire" effect. IOW, you, the fence, and the ground would be at the same potential.
If you are actually on the bonding grid, you are fine, but if you are on the earth even a short distance from the bonding grid, you will be shocked.I was thinking more on the lines of standing on the bonding grid and motor and fence were bonded.
If that is the case why did they do away with the mat grid setup and allow one run 18" - 24" away from the pool. Sounds like that is worthless unless you are standing on the wire. That makes no sense
Roger
There was no technical substantiation to eliminate the grid and permit the use of a single bonding wire.If that is the case why did they do away with the mat grid setup and allow one run 18" - 24" away from the pool. Sounds like that is worthless unless you are standing on the wire. That makes no sense
In a correctly installed system the fault should be quickly cleared. If you are in the water, you are probably ok under fault conditions, but if you are trying to get out of the pool by touching the concrete deck under fault conditions, you probably are not going to make it.Well we never hear about entire pools with floating bodies so either there is never a fault or something else is up.
The same thing could happen with an open utility primary or secondary neutral in the area, but in that case the high voltage could last for an extended time as there is nothing to clear that type of "fault".
There may be voltage gradients in the water and between the water and the bonded metal parts. I am not sure how conductive the pool water is as compared to that of the earth.You can be in the water and touching the floor of the pool as in the lower end or a kiddie pool. Many kids hold on to the ladders etc. Wouldn't there be a potential difference between the bottom of the pool and the water itself-- to some degree at least.