jwelectric
- North Carolina
After doing a search I find all the threads are closed so I started another to rehash the EBG around bodies of water namely hydromassage tubs.
Bonding requirements first appeared in the 1999 edition 680-73 and was versed; All metal piping systems, metal parts of electrical equipment, and pump motors associated with the hydromassage tub shall be bonded together using a copper bonding jumper???..
This was moved to 680.74 in the 2002 cycle but the verbiage stayed the same.
In the 2005 edition the verbiage was changed by a proposal by the TCC to read; All metal piping systems and all grounded metal parts in contact with the circulating water shall be bonded together????
This brought forth a debate concerning the word ?and? and whether or not it was a compound sentence meaning all metal pipes plus anything in contact with the water.
During the 2008 cycle verbiage was added to state that this #8 was not required to extend to a panel or electrode but the debate of the intent of the first 15 words of that section continued in debate.
Here is the Staff Note included with NECPlus; The bonding required by 680.74 is intended to create a local equipotential plane, and the equipment grounding conductor of the branch circuit supplying the hydromassage tub provides a path for ground-fault current.
In the 2011 cycle the verbiage was once again changed to include: The 8 AWG or larger solid copper bonding jumper shall be required for equipotential bonding in the AREA of the hydromassage bathtub and shall not be required to be extended or attached to any remote panelboard, service equipment, or any electrode.
Now to the questions at hand, does the #8 that has been required at a hydromassage tub for the past five code cycles require any metal pipes in the ?AREA? of a tub to be bonded or does it mean that no EBG is required at all?
Is it only anything that is in contact with the water in the tub or does it include the water that is associated with the tub such as the mixing valve used to fill the tub?
Is this a compound sentence which says; All metal piping systems shall be bonded and all grounded metal parts in contact with the circulating water shall be bonded together?
Thank you for taking the time to read this lengthy post and responding.