JS-Addis
- Addis, Louisiana
Has anyone installed manufactured equipment that was identifiedfor the area classification, but the wiring or devices didn't meet the requirements set forth in Art. 502?
Thanks Bob for your response. Actually, the last sentence in your response summed up what I was hinting at. The piece of equipment is a bag heat sealer. The heat sealer is indentified for the area classification, Class II, Div I, but it doesn't meet NFPA 70, Art. 502, Class II, Div I wiring methods.
The question is it normal to run into a piece of equipment that indentified, but doesn't meet the wiring standards for NFPA 70.
Thanks,
Bob to answer your question, they didn't use any of the wiring methods called out in Class II, Div I. Instead they used single conductor cable installed in plastic corrugated flexible tubing, similar to what you would find at Auto Zone. The reed switches, used as position switches for pnematic cylinders, are hermetically sealed but not listed or labeled for the area classification.