We have a communication building at a site with 2 buildings. The site is fed with 120/208 3 ph service to a meter bank. The building that we have our equipment in is going to be moved out and we are going to move one of our prefab buildings in. Our prefab buildings are 120/240 sp. I have priced a 3 ph to 1 ph transformer for the building but am now being ask if the building can be hooked up 208 sp. It is not a problem with our A/C units, they are slash rated, the UPS and the microwave rectifier. My concern is what the unbalance will do/can do the the utility transformers. The other building on the site will remain 3 ph. The load on our building will be around 80-100 amps. What do you think?