Just wondering how many guys think that "it was existing" is an acceptible arguement?
I looked at a job this week where the "electrician" had rewired a house, added a new distribution panel and run his feeder from an existing main service (100 amp main breaker only). The first thing I noticed was he ran his feeder as a 3 wire in conduit, OK. So I asked him to open the main panel and there was no GEC, no ground rods and the neutral was isolated. So there was no bonded metal anywhere in the house, and the guy kept parroting "it was existing" over and over, even after I explained to him that there would be no way for a fault to ground to clear the way it was set up. Needless to say, it's getting a GEC and ground rods.
I looked at a job this week where the "electrician" had rewired a house, added a new distribution panel and run his feeder from an existing main service (100 amp main breaker only). The first thing I noticed was he ran his feeder as a 3 wire in conduit, OK. So I asked him to open the main panel and there was no GEC, no ground rods and the neutral was isolated. So there was no bonded metal anywhere in the house, and the guy kept parroting "it was existing" over and over, even after I explained to him that there would be no way for a fault to ground to clear the way it was set up. Needless to say, it's getting a GEC and ground rods.