Why run 3/0 cu for residential 200A service?

Status
Not open for further replies.

Flatpad

Member
Location
NJ
Why would someone run 3/0 cu for a residential service? I've have now seen this for the third time and have to ask. I have been to 3 separate houses, all built in the last 4-6 years, all done by different electrician. The only thing that is similar is that the houses are all powered by JCP&L, I usually work in PSE&G territory.

What reason would someone have to use the bigger wire? I could understand seeing 1 house like that, maybe the contractor had some left over. But 3...? :D
 

iwire

Moderator
Staff member
Location
Massachusetts
Perhaps the homes where supplied 208/120 utility source.

As you can see you can only use the smaller conductors if it is a 120/240 service.

(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services
and Feeders. For individual dwelling units of onefamily,
two-family, and multifamily dwellings, conductors,
as listed in Table 310.15(B)(6), shall be permitted as
120/240-volt, 3-wire, single-phase service-entrance conductors,
service-lateral conductors, and feeder conductors
that serve as the main power feeder to each dwelling unit
and are installed in raceway or cable with or without an
equipment grounding conductor. For application of this section,
the main power feeder shall be the feeder between the
 

Flatpad

Member
Location
NJ
These were definitely 120/240 services, I tested the voltage on 2 of them for other reasons, and they were right smack in the middle of suburbia :D

I guess it was just a coincidence. :thumbsup:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Years ago I did that from the meter to the panel when they were side x side because I did so many 400 amp services with 2- 200 amp panels that 3/0 is required. I always had pieces of 3/0 and copper was cheap so I would use it rather than go to the supplier to get 2/0. Saved time
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
it would not surprise me at all to find that whoever decided such things decided not to stock 2/0.

the guy in charge here refuses to buy #3 for some reason so if I need #3 I get #2, sometimes even if I put #3 on the BOM.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
= =

Had an electrician tell one time, that the larger size was for future
expansion, ..."if" they decided to add more stuff later.

& &

It is amazing to me how many os us EC got licenses and did not know squat. I remember being told so many wives tales that I took them as gospel. I don't believe any of them were correct.

Two that come to mind is 100' run of conduit and a JB was needed and the other was that the neutral could be dropped one size. Well we know that the 100' rule is not correct and the other one could be true but if the calculated load was less the neutral could be as small as the GEC- a #4 for a 200 amp service.
 

Flatpad

Member
Location
NJ
I still hear long time electrician, some of them with contractor licenses, saying how you can't splice in a panel. :jawdrop:
 