If the power dissipated in the coil is greater at 208 than at 240 then the life of the coil insulation will be shortened but coils can take a lot of abuse.
You may need a scope and shunt to confirm this.
If you have an IR meter or thermistor or thermocouple you may be able to see a temp. rise in one case over the other.
 