Does anyone know where/if in the ADA inside corners are addressed in regards to FA pull stations locations?
 
Seems like conflicting Codes. Is it not that interior fire alarms pull stations are at the exit of a space?

The height of a standard pull alarm is with-in the arms reach of the wheel chair bound!

I'm missing something ?

OK, no I've never heard of that requirement for "that" height, elevator buttons Yes...
 
Last edited:
Picture walking towards an exit door: 12" to the left from an outside wall, open to the right.

The pull station is on the outside wall 6" from the corner.


Height is not a issue.
 
It's within 5' of the opening in nfpa 72. It was hinted at me you can't be within 18" of an inside corner, for ada
 