Does an open delta have the same voltage between the legs where the transformer is missing?
On paper, it looks the same as 208Y/120 that is fed with two legs and a neutral.
It was explained that open delta allows continued service with one of the three transformer out of service.
Assuming
A
CB
order
In a closed delta, A-B, B-C and C-A are 240v.
If secondary on A-B burns out, what's the voltage between A-B?
Would they add up to 416v as if its two of the three windings on 416Y/240 system?
How is it any different from this with s3 not pulled in?( As in individual tenant suite in an office building)
On paper, it looks the same as 208Y/120 that is fed with two legs and a neutral.
It was explained that open delta allows continued service with one of the three transformer out of service.

Assuming
A
CB
order
In a closed delta, A-B, B-C and C-A are 240v.
If secondary on A-B burns out, what's the voltage between A-B?
Would they add up to 416v as if its two of the three windings on 416Y/240 system?
How is it any different from this with s3 not pulled in?( As in individual tenant suite in an office building)