hillbilly1
- North Georgia mountains
- Owner/electrical contractor
MD posted a typical installation book (Even with the newer Nexus control system) that is supplied with all Generac RTS type transfer switchs, the wiring diagram (page 9-11) in this PDF is typical of of all Generac RTS ATS wire ups, the only exception is the change of battery charger system and where it is located, when they used to supply the wall wart type (no plug just the lamp cords coming out of it)
At one time the instruction had us installing them in the generator cabinet at the battery, and supplying it with a circuit from the house panel, later they supplied the terminals and a fuse block to connect them in the transfer switch with a tap to one of the load terminals and neutral, they even included the screw and male spade terminal to do this, and the charger output hooked to 194/15B + and 0 - this back fed the battery through these terminals, the 0 terminal is also tied to the cabinet of the generator for a negative grounding of the battery, when they came out with the Nexus controller they built a float charger system right on the main mother board in the generator, so no external charger is needed.
There is a 178 and 183 terminals on some Generac generators, in most cases you will not use them, they are for remote switch automatic starting for use with a manual transfer switch
The electronics is all in the generator, the main controller board is located in the metal box behind where you land your wires, it will have a cover over it, N1 and N2 are an input to this controller and 23 is a -12vdc output to the transfer switch TR relay (ice cube relay) 194/15 is just the positive from the battery that also runs through the 7.5 amp fuse on the generator switch panel, the battery supplies all the power for the controller and the power up to the TR relay, the TR relay switches the set of solenoids that pull the transfer switch one way or the other, these are DC coils fed through a full wave bridge rectifier from the line voltage (240vac), the power to transfer to generator is derived from E-1 and E-2 which is the hots from the generator, this is to keep the transfer switch from transferring to the generator if it is not running or the breaker on it is tripped or off, the transfer to utility coil is fed through the same bridge rectifier but the limit switches will now have it connected to the N1A and N2A which is the utility side of the transfer switch, again if there is no utility power it will not transfer back.
I would presume that the input to the main controller board could be of a high enough impedance that N1 and N2 could pick up some capacitive coupling and if this happens while generator is running it could trigger the system to think that power is restored and transfer back, this could cause it to start cycling back and forth??? that is about the only thing I could see happening, but if it did it could be bad?
That's what's strange about Generac, everybody else has the brains in the transfer switch. Even if there was enough capacitive coupling to fool the controller, there would be a delay in transfer and with the absence of utility would prevent the utility side solenoid from actuating regardless of the dc relay state once it is on generator power. The only possibility would be the generator times out on cool down, and shuts off. That might start the cycle again, but not likely because since the charger comes off the same source as N1 and N2, the impedance should be low.