JJsparks
- N Michigan
I posted a question a couple of months ago reguarding voltage drop for a run of light poles that I am installing. Many replies very helpful and got me going in the right direction. I would like to confirm my thinking on wire sizing since once its done theres no turning back.
A typlical run has about 10 incandescent poles, each pole drawing 150 watts each. The closest pole from the soure is 400 feet, each additional pole is approximately 80 feet down line from the next. My thinking is I calculate the first pole at the total load of the entire run( 10 x 150 watts = 1500). I come up witha number 6 use copper for the correct sizing. My next step is to calculate the next pole using the longer wire length but with the load reduced by one fixture or 1.23 amps. I would continue to use this method until I am at the last post where I will have a sigificant wire length but only a load requirements of 1.25 amps. Is my thinking and calculations correct or am I off base. Thank you for any help you may provide.