Davebones
Senior Member
- Location
- North Of Tampa Fl
Have a ( Mitsubishi FR-F740-00770-NA ) 50 HP drive . The nameplate show's " Input 115 A " . The drive's only rated for output of SLD of 77 amps . Looking at 430.122 we would then size the feed to the drive for 144 amps ? So we would need to have a 1/0 feed. Would a disconnect rated for 100 amps be sufficent or do we need to up the size because of the increase in feeder ?